I recently purchased an SYL-2362 PID and a PT100 from Auber Instruments (great service â highly recommended by the way). When I came to use the setup though (the sensor is in a brewing boiler away from direct heat sources) it gave a fluctuating temperature reading. When the wort was boiling - the temperature reading constantly varied from 92C to 104C, cycling up and down in a 1 - 2 second cycle. Removed from the liquid though it showed a steady and correct temperature when in open air. Mystery I thought :?
I contacted Auber today and they (Suyi Liu) got right back and said that there is a line filter in the controller for 50Hz AC power. You can change it to UK 50Hz - just press the SET key, enter code 1262. Then, Set 5060=0. The default is for US 60Hz (=1)
Problem instantly solved â whenever it was in use it was picking up the mains and the filter didnât get rid of it until changed to 50Hz. Donât recall seeing anything in the manual about it so thought that you guys might like to know too if you use Auber
I contacted Auber today and they (Suyi Liu) got right back and said that there is a line filter in the controller for 50Hz AC power. You can change it to UK 50Hz - just press the SET key, enter code 1262. Then, Set 5060=0. The default is for US 60Hz (=1)
Problem instantly solved â whenever it was in use it was picking up the mains and the filter didnât get rid of it until changed to 50Hz. Donât recall seeing anything in the manual about it so thought that you guys might like to know too if you use Auber